Large home new service-under 400 amp calc. load. 3-200 amp panels for house. JCP+L wont supply CT w/ low load calc. Inspector states IF CT is allowed from JC; main disconnect (fuses or non-fused ?)must be installed ahead any service size over 400 amps-including residential. I'm looking @ art. 230(services disconnecting means); and cant seem to locate this demand of a disconnect in this article. Inspector suggested a I-Line 400 amp ML panel w/ 3-200 amp breakers ahead of the existing panels to accomodate the three 200 amp panels so to not exceed 400 amps. Problem is ; No physical room
for the enclosure w/three panels.