Re: Main Disconnect
I agree that there is no "lockable" requirement under NEC, unless exceptions to "in sight" requirements are used for:
1)controller over 600v --- 430.102a except.1
2)motor uses controller disconnecting means as motor disc. means --- 430.102b except.
There may, however, be other lockout requirements under OSHA LO/TO. In addition, NFPA 70E, Standard for Electrical Safety Requirements for Employee Workplaces; or NFPA 79 Electrical Standard for Industrial Machinery, may (I'm not 100% sure) have "lockable" requirements that could also be enforced by OSHA.
Len