Main Disconnect

Status
Not open for further replies.

chadsundberg

New member
Location
North Dakota
The main disconnect switch is about 30' away from the control panel. The control panel operates two submersible pumps for a lift station. The pumps have circuit breakers in the control panel. Is there a restriction on how far away the main disconnect switch can be?
 

rick5280

Senior Member
Re: Main Disconnect

I believe that the two units must be within sight (up to 50' apart)of each other. See Article 430-102(A)

Rick Miell
 

Len_B

Member
Location
New Hampshire
Re: Main Disconnect

Unless the two circuit breakers are operable with the control cabinet closed and disconnect their respective pump motor control thus serving as the controller disconnecting means; the main disconnect would become the "controller disconnecting means" and would have to be "in sight" (and less than 50 ft per art. 100 - definitions) of the pump motor controls. art.# 430.102a

[ February 20, 2003, 07:20 PM: Message edited by: Len_B ]
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Main Disconnect

There is no NEC requirement for a "lockable" disconenct when the disconnect is within sight of the equipment served by the disconnect.
Don
 

Len_B

Member
Location
New Hampshire
Re: Main Disconnect

I agree that there is no "lockable" requirement under NEC, unless exceptions to "in sight" requirements are used for:
1)controller over 600v --- 430.102a except.1
2)motor uses controller disconnecting means as motor disc. means --- 430.102b except.

There may, however, be other lockout requirements under OSHA LO/TO. In addition, NFPA 70E, Standard for Electrical Safety Requirements for Employee Workplaces; or NFPA 79 Electrical Standard for Industrial Machinery, may (I'm not 100% sure) have "lockable" requirements that could also be enforced by OSHA.

Len

[ February 21, 2003, 05:04 PM: Message edited by: Len_B ]
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Main Disconnect

Len,
I don't think so. OSHA permits tag out without a lock. The utility in our area does not permit the use of any locks on disconnects within their generating plants. Yes, they are not under the NEC, but they are covered by OSHA.
Don
 

Len_B

Member
Location
New Hampshire
Re: Main Disconnect

Don,
Thanks. I wasn't sure about possible OSHA requirements that might apply to this specific situation.
In addition to "in-house" tag only policies, many times locks simply can't be attached, requiring tag out only. BTW, If "tyrap" alone is used for LOTO, I believe it must be 50 pound rated (Code ref ?)

Len
 