MAIN ELECTRICAL POWER CONNECTION

Status
Not open for further replies.

i.qasim

Member
Location
Saudi Arabia
b4a69c6c-22c0-433b-b615-c9c450d8f6cb-medium.jpg

as I have tried to show in the pic, my question is,... can we do that?

lets suppose a scenario,

I have incoming cable say 300 mmsquare, splitted into three connections say 100 mmsquare(suppose)

I have an electrical energy meter installed on each of the three connections, supplying 60 A each.

the problem is... I have a load that requires more than 60 A.

Can I re-unite the cables to one cable respecting the color codes etc, and get my required power?

*** It's a rush project and we dont want to do all the process of service provider again.
 

iwire

Moderator
Staff member
Location
Massachusetts
Not allowed under the NEC.

You would have overcurrent devices and conductors in parallel that are prohibited from being in parallel.
 

i.qasim

Member
Location
Saudi Arabia
Not allowed under the NEC.

You would have overcurrent devices and conductors in parallel that are prohibited from being in parallel.

How?

I mean, it is same as having multi cores for each phase,
which is allowed.

we only have energy meters in the path :(

let me rephrase my question:

does an energy meter placed in between two points A and B, changes anything like phase, voltage, current attributes of electricity from A to B? or Not!
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
As Bob says, the upstream OCPD's will be in parallel when you do this which is a violation of NEC 240.8

Roger
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
How?

I mean, it is same as having multi cores for each phase,
which is allowed.

we only have energy meters in the path :(

let me rephrase my question:

does an energy meter placed in between two points A and B, changes anything like phase, voltage, current attributes of electricity from A to B? or Not!

You are in Saudi Arabia. I would imagine our NEC would not apply. You may have a similar restriction in your codes however. We would not be a good source for that.

As to the metering, there is no noticeable effect on a circuit from running it through a CT, assuming that's what you mean. Whether or not it shares the load equally is debatable. Even a slight difference in resistance of a connection will have an effect on current sharing, and you have a lot of connections in this scheme.
 

Haji

Banned
Location
India
I have incoming cable say 300 mmsquare, splitted into three connections say 100 mmsquare(suppose)
If the splitting of incoming cable say 300 mmsquare is done in a panel, the load requiring more than 60A may be tapped from the panel through an energy meter.
 