Hi gentlemen
I have read in EC&M web magazine an article written by Mr. Mike Holt about Motor calculations .See this link http://www.ecmweb.com/mag/electric_motor_calculations_part_2/index.html
The last example shows the main feeder size is 6 AWG (with ampacity of 65 A as in Table 310.16) and the breaker size for the same feeder is 80 A Breaker.
Is this permitted? I mean is it permitted that breaker size ampacity is larger than cable ampacity?
Is this applicable also for main breaker of houses? Which NEC article discusses Size of Main Breaker of Houses?
My Q assuming the houses contains Window Air Conditioners, Water pump, lightens?etc.
Thanks