In Informative Annex D, there is an example (example D5(a)) of a standard calculation for the main feeder load for a multifamily dwelling from a 208Y/120V service. In this example, the range load (29000VA) is divided by 2 (to find per-phase demand) and multiplied by 3 (to calculate equivalent 3-phase load). It's not clear to me why this is necessary as there appears to be no requirement for this step in 220.55.
Furthermore, there is no consideration of equivalent 3-phase load in the optional calculation (example D5(b)) which follows, which is a very similar scenario with a multifamily dwelling served by 208Y/120V.
I have a homework problem that requires me to do standard and optional calculations for a similar scenario, and my main load results were drastically different between the two because the optional calculation apparently doesn't require me to find equivalent 3 phase load...
So my question... is example D5(b) wrong?