I do not believe you will ever find a code requirement that the 'main protective device' actually be inside of the panel.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If you read Jim's response you'll see that your questions are so broad that there isn't really an answer. Do you have some specifics in mind as far as the type of installation? One example would be, you can use a MLO panel if there is an OCPD ahead of the feeder and in the same building. One could install a MLO on the 10 floor of a building with the OCPD ahead of the feeder in the basement service equipment.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
I take the OP to be asking more of when do you need a main breaker/disconnect at or in the panel, and when can you leave the feeder breaker in the switchboard, MCC, panelboard, or wherever it is fed from and just use a MLO.

Perhaps some clarification on the specific project set-up is in order.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Because of how vague the question is, the only viable generalized answer in my opinion is that it is NOT OK to install an MLO panel when there is no other suitable OCPD in the circuit. Everything else is subject to specifics of the installation.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
A service panel must be service rated and can have up to 6 throws-- dp breaker is one throw-- of the hand to disconnect the structure. So , in a sense, you never need a main breaker. Often there is a main breaker at the service panel and then main lug panels after that. The exception would be a sub panel in a detached structure that may also have a main breaker panel but the 6 throw rule applies there also.
 

27hillcrest

Senior Member
Sorry to be so vague guys. I wanted to know when do have to have a main breaker in a sub panel that is in the same building? From some of the responses it seems like NEVER if it is in the same building as long as the OCP is installed on the feeder.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sorry to be so vague guys. I wanted to know when do have to have a main breaker in a sub panel that is in the same building? From some of the responses it seems like NEVER if it is in the same building as long as the OCP is installed on the feeder.

No apologies necessary.

Yes, that's correct, sort of. Even if an OCPD were required at the panel it wouldn't need to be a main CB it could be a fused switch or other OCPD located adjacent to the panel.
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
I would think more along the lines of convenience. Is it required, maybe not, but would it be nice to have from a maintenance perspective, maybe. If it is located in a large building where it might take a while to track down somebody down and locate the right OCPD then probably would be nice. Industrial where you have lockout/tag-out requirements and everything is well labeled, and only the plant electricians touch the stuff, then probably not.

Remember NEC is MINIMUM safety requirements; it is not a practical design guide.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Also be aware, that a requirement for a disconnecting means (i.e. LOTO at an out building) does not mean it must be an overcurrent protective device like a 'main breaker'.
 