As long as I have a "Main Breaker" outside at the meter, isn't it alright to put a "Main lug" panel on the interior? Wonder if someone can give me the reference in the code for this? This has been my understanding all my electrical experience, but haven't traced it to the actual code reference. Thanks
Also, if running a 100 amp. 4 wire feeder to an inside panel, as long as I've got it fused correctly at the Mains, can't I use a 200 amp main breaker panel (if desired) for the inside? In other words the 100 amp breaker that will be protecting the feeder will trip (if needed) before the 200 amp will.
The 200 amp would only be serving as a disconnect, not as overcurrent protection. Thanks again
Also, if running a 100 amp. 4 wire feeder to an inside panel, as long as I've got it fused correctly at the Mains, can't I use a 200 amp main breaker panel (if desired) for the inside? In other words the 100 amp breaker that will be protecting the feeder will trip (if needed) before the 200 amp will.
The 200 amp would only be serving as a disconnect, not as overcurrent protection. Thanks again