T tonype Senior Member Location New Jersey Jun 24, 2018 #1 4 family home with 5 meters - one for each dwelling and one for the "owner". Each has a main circuit breaker. Is a main disconnect required for the entire building (before the meters )?
4 family home with 5 meters - one for each dwelling and one for the "owner". Each has a main circuit breaker. Is a main disconnect required for the entire building (before the meters )?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 24, 2018 #2 No, you are permitted to have up to 6 service disconnects grouped together.
T tonype Senior Member Location New Jersey Jun 24, 2018 #3 infinity said: No, you are permitted to have up to 6 service disconnects grouped together. Click to expand... Thanks
infinity said: No, you are permitted to have up to 6 service disconnects grouped together. Click to expand... Thanks