elecmen said:Installing sub panel in out building. There is going to be 3 circuits. Question is a main breaker required by code or can I use main lug panel as long as there in no more than 6 circuit breakers?
stickboy1375 said:The problem is that your panel is most likely a Lighting and Appliance Branch Circuit Panelboard, and that requires to be protected by not more than two main circuit breakers.
RUWired said:Although if he used all 2 pole 60 breakers, this would be a power panel board, making this senerio inpractable...
stickboy1375 said:I would just install a 60 amp main breaker and be done with it.
RUWired said:What i'm saying is , if he met the requirement of using the 2 pole 60 breakers, then he would'nt be able to use the panel like he wanted to.I agree , just use the one 2pole 60 and be done with it.
louisfulleriv@yahoo.com said:Being a new comer to Mike Holt's forum, and reading such good info is very enjoyable thank you.
stickboy1375 said:The problem is that your panel is most likely a Lighting and Appliance Branch Circuit Panelboard, and that requires to be protected by not more than two main circuit breakers.
jwelectric said:He also said that was an out building which brings 225.30 throught .39 into the game. The exception to 408 will not apply now.
suemarkp said:Why does 408.xx not apply to an outbuilding panelboard? If its a feeder it has upstream overcurrent protection. What in 225.30 through 39 requires a single disconnecting means at an outbuilding? I see a 6 handle disconnecting means specifically allowed in 225.33(A)
augie47 said:unless he is under the '08 code, in which case, I believe there is no such thing as a L&A panelboard.
correct ?
jwelectric said:225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
Read the part on that panel where it makes the statement;
"SUITABLE FOR USE AS SERVICE EQUIPMENT"