Do you need a main or not? A second building on same property as house. It has a panel in it with 4 circuits in it.
The way I look at it per 225-32 of the NEC you need main disconnect inside or outside nearest the point of entrance. The NEC 225-36 says it must be rated as service equipment.
The kicker is the use, is it for lighting and appliance. I think by definition of lighting and appliance panel board it is.
So, I think it needs a main breaker.