main overcurrent protection in subpanel

Status
Not open for further replies.

smallfish

Senior Member
Location
Detroit
Is it required by the NEC to provide main overcurrent protection in a sub-panel for feeders?
The feeders in question are fused and supplied from a distribution panel in the basement of a mall and run in pipe 250 feet through a floor to this subpanel that supplies circuits for a kiosk (for lack of a better word, a boutique).
 
You are not required to have a main breaker in a sub-panel where the feeder feeding the panel has it's overcurrent protective device at the distribution panel.

Chris
 
My head always gets twisted on this one. What is the panel called then? It isn't metered seperately. I'm MORE than willing to look it up! Just need a tiny hint. (Have '05 and '08 right here next to me)
 
andinator said:
My head always gets twisted on this one. What is the panel called then? It isn't metered seperately. I'm MORE than willing to look it up! Just need a tiny hint. (Have '05 and '08 right here next to me)

I don't know that it has a name per se but I would call it "the panel in the garage"..:grin: or maybe main feeder panel for detached garage..:smile: :smile:

Remember sub panel is not in the NEC either.
 
andinator said:
Even in a detached garage in a dwelling unit?

A panel in a garage needs to have a disconnecting means at the garage (See 225.31). 225.31 is not a requirement for an overcurrent device at the detached garage just a disconnecting means which could be a main breaker but can also be done by the use of a non-fused disconnect.

Chris
 
I agree that the term "sub-panel" is confusing especially due to the fact that the NEC doesn't use the term.

I try to avoid the use of the term "sub-panel" and just call it either a power panel or lighting and appliance panel.

Chris
 
Even in a detached garage in a dwelling unit?
Even there the panel is not required to have a main breaker, but the building is required to have a disconnect. The easiest way to provide the required building disconnect is to install a main in the panel.
Don
 
don_resqcapt19 said:
Even there the panel is not required to have a main breaker, but the building is required to have a disconnect. The easiest way to provide the required building disconnect is to install a main in the panel.
Don



Sure as long as 225.32 are satisfied....
 
I have a pic of a 100amp main lug panel in a detached garage that has no disconnect and the there is no connector were the feeders come in the back of the panel, just pipe that ends in the wall, the wire pass through some insulation, 1/2" osb, and through a open KO. Its fed by undersized USE too

Best part is it passed inspection. Sticker and all.
 