Main Panel 400 Amp - How to measure capacity -

Status
Not open for further replies.

hardworker

Senior Member
Main panel 400amp 120/240 single phase 3-wire service

Clamp meter shows 180 amps being drawn on phase A. Clamp meter shows 190 amps being drawn on phase B.

Will the main breaker of 400amp capacity trip when the total of both phases exceeds 400 amps?

OR

Will it trip only when either of these two phases exceeds 400amp?
 
Yes... but that depends on perspective. It is only true at the instance you measured. If you are attempting to evaluate whether loads can be added, your measured values will likely not indicate how much of the system is available. The NEC requires determination through 1) load calculation, 2) month-long monitoring for peak demand, or 3) POCO demand data.
 