mmm_max
Member
- Location
- ridgecrest,ca
Since a main breaker furnishes current to two phases of the panel, will it trip if all the current is on one leg. For example a 100 amp residential breaker with drawing 150 amps on one side only?
Yes. A two pole breaker (main or otherwise) is two single pole breakers with a common trip mechanism that disconnects both of them if either one trips.Since a main breaker furnishes current to two phases of the panel, will it trip if all the current is on one leg. For example a 100 amp residential breaker with drawing 150 amps on one side only?
That's a common misconception among folks who haven't dealt with power distribution. I can remember having to grasp the way it works, myself, even after I got my EE degree.That being said, I once asked this silly question way back: "If you have a 60 amp 3 pole breaker, is it 60 amps per phase or a total of 60 amps from all the phases....lol. " What a numb nuts.
No.If I was not concerned about inspection or the NEC at all; and assuming a 100 amp main breaker panel and assuming that the main will trip if 100 amps is exceeded, could I not size the wire feed for the two mains for 50 amps if the two circuits are balanced?
This is being discussed and answered: Thread 'argument with electrician' https://forums.mikeholt.com/threads/argument-with-electrician.2569893/.If I was not concerned about inspection or the NEC at all; and assuming a 100 amp main breaker panel and assuming that the main will trip if 100 amps is exceeded, could I not size the wire feed for the two mains for 50 amps if the two circuits are balanced? ......
Another way to say it is, it is capable of supporting 24,000 watts whether it is 120V or 240V or a combination of both. With that said this appears to be a DIY thread so we will close it based no the forum rules.Thanks Jon. Your explanation clarified the situation well. So when I buy a 100 amp main distribution panel it is actually capable of supporting 200 amps in total including both legs. Got it!
This site is designed for:
* This NEC� Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.
- Electrical Contractors
- Electricians
- Engineers
- Inspectors
- Instructors
- Other electrically related individuals
We still get that in here once in a while from the DIY crowd that we remove from view because they are not in the trades. In unmoderated forums like Reddit, it’s a very common question still.…
That being said, I once asked this silly question way back: "If you have a 60 amp 3 pole breaker, is it 60 amps per phase or a total of 60 amps from all the phases....lol. " What a numb nuts.