julesm

Member
Greetings,
in a new building what is the correct way to size a main panel with subpanels and transformers? I have four 100A load breakers on my main dist panel:(2) 75kva transformers and (2)100A subpanels. How should I size the main?
Pleez help.
Thank you,
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
panel

panel

smart*** answer would be by Art 220 :)
seriously, you would need to look at specific loads plus the requirements of 220.3.
Assuming you are looking at a 480v3phase panel (with 3 phase breakers), the 100 amp breakers to the 75 kva might be a bit on the low end, but if the transformers are loaded, a 100 amp load per transformer would be a "good" number.
As far a the other two panels, you, agan would need to look at the actaul load. If you are trying to cover from the end user's standpoint, I guess figure 100 amps for each load, although the transformers might exceed that a bit.
 
Last edited:

julesm

Member
I was trying to simplify the question and therefore wasn't clear...:rolleyes:
Art 220 is a big help, of course.
My confusion I think is that the initial loads are small, so I don't want to terribly undersize my service.
So with, as in my simple example, let's assume each 100A panel and transformer has a connected, let's say continuous, load of 30A.
30 x 1.25 = 37.5A
37.5A x 4 = 150A.
So I could use a 150A service to comply with 220. But that leaves no room for future growth. So maybe I'll do a 300A panel.
My question ultimately is, when future growth is unknown, how do you decide?
Thanks,
JM
 

GilbeSpark

Senior Member
Location
NC
Is this a product you're providing for a customer? If so, ask them what they want.

Is this something for a company you work for? If so then plan for the future. A few extra dollars now can save the company more down the road, plus the hassle of having to upgrade later on.
 