hey all. we have an application where the electrician put in a generator and auto transfer switch, thus rendering the main panel (200a homeline main breaker panel) into a subpanel. i'm having a back and forth with the electrician, the inspector, and siemens as how to properly isolate neutrals and grounds in this panel, now that the ATS is the first point of disconnect.
i've had multiple conversations with Siemens tech support. first time they told me an auxiliary ground bar was required. second and third time they told me that pulling the bonding screw was all that was needed. the electrician also said that pulling the bonding screw as well as pulling the screw that attaches the neutral bar to the bar that runs behind the main lugs was all that was needed. with all this done, i still get continuity between the neutral bar and the ground bar.
additionally, i'm wondering if the way the 2/0 ground from the ATS is bonded to the rest of the ground bar is correct? it's just supposed to be bonded via the panel and the tiny screws at the top of the ground bar and at the ground lug the 2/0 ground lands on?
unfortunately the catalog number for the panel is inaccessible so i can't get specifics, but wondering if anyone has thoughts based on the picture i'm putting below.
![IMG_3930.jpg IMG_3930.jpg](https://forums.mikeholt.com/data/attachments/26/26515-6c7ab7a7d7942864961c263f61875d7e.jpg)
i've had multiple conversations with Siemens tech support. first time they told me an auxiliary ground bar was required. second and third time they told me that pulling the bonding screw was all that was needed. the electrician also said that pulling the bonding screw as well as pulling the screw that attaches the neutral bar to the bar that runs behind the main lugs was all that was needed. with all this done, i still get continuity between the neutral bar and the ground bar.
additionally, i'm wondering if the way the 2/0 ground from the ATS is bonded to the rest of the ground bar is correct? it's just supposed to be bonded via the panel and the tiny screws at the top of the ground bar and at the ground lug the 2/0 ground lands on?
unfortunately the catalog number for the panel is inaccessible so i can't get specifics, but wondering if anyone has thoughts based on the picture i'm putting below.
![IMG_3930.jpg IMG_3930.jpg](https://forums.mikeholt.com/data/attachments/26/26515-6c7ab7a7d7942864961c263f61875d7e.jpg)