-200a single phase service
-Exterior underground feeder to a meter
-Offset nipple from meter to 200a 3R disconnect
-PVC sleeve from back of disconnect to 200a main lug subpanel
-UFER #4
-Ground rod #6
-Gas bond #6
-Intersystem bond #6
Question: We run the UFER gec to the main disconnect neutral and run the other grounds/bonds to the subpanel and then run a #4 from the service disconnect to the ground bar in the sub panel. Building Inspector is telling us that we have to run both the UFER and ground rod GECs directly to the service disconnect. Is there an issue with either way?
-Exterior underground feeder to a meter
-Offset nipple from meter to 200a 3R disconnect
-PVC sleeve from back of disconnect to 200a main lug subpanel
-UFER #4
-Ground rod #6
-Gas bond #6
-Intersystem bond #6
Question: We run the UFER gec to the main disconnect neutral and run the other grounds/bonds to the subpanel and then run a #4 from the service disconnect to the ground bar in the sub panel. Building Inspector is telling us that we have to run both the UFER and ground rod GECs directly to the service disconnect. Is there an issue with either way?