Attached sketch shows main service panelboard with main circuit breaker that has incoming 3#3/0 AWG incoming service conductors.
I am aware that one can have one bonding jumper from neutral bus bar to the panelboard enclosure.
However, the attached sketch #4 main bonding jumper between neutral bar and ground bar, shows #4 bonding jumper from ground bus bar to the panelboard enclosure and another #4 bonding jumper from neutral bus bar to the panelboard enclosure.
Does NEC 2014 code allow or does not allow one bonding jumper from neutral bar to panelboard enclosure and another one from ground bus bar to panelboard?
I am aware that one can have one bonding jumper from neutral bus bar to the panelboard enclosure.
However, the attached sketch #4 main bonding jumper between neutral bar and ground bar, shows #4 bonding jumper from ground bus bar to the panelboard enclosure and another #4 bonding jumper from neutral bus bar to the panelboard enclosure.
Does NEC 2014 code allow or does not allow one bonding jumper from neutral bar to panelboard enclosure and another one from ground bus bar to panelboard?