C codequestion Banned Location MD, USA Mar 26, 2018 #1 Attached pdf does the configuration shown require main service disconnect per NEC 2014? Attachments Document1.pdf 91.8 KB · Views: 0
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Mar 26, 2018 #2 The code requires either 1 main disconnect or up to 6 disconnects for the service or feeder to a separate structure. Your diagram has the latter
The code requires either 1 main disconnect or up to 6 disconnects for the service or feeder to a separate structure. Your diagram has the latter