IMO. Not Code compliant as a non-service rated transfer switch is not one items allowed ahead of the service disconnect.
Please see image attached, will this be code compliance as the ATS does not have main breaker, ATS is grounded as service entrance.
Both ATS and MSA are in same room. Thank you!
I thought you still needed a separate disconnecting means. I'll have to look it up.I believe that 230.82(5) allows circuits for standby power systems to be installed ahead of the service disconnect. Your referenced drawing seems legit.
The I read that rerference is "taps to supply ,,, circuits for standby power...." not for ATS systems... (I could be wrong)I believe that 230.82(5) allows circuits for standby power systems to be installed ahead of the service disconnect. Your referenced drawing seems legit.
The I read that rerference is "taps to supply ,,, circuits for standby power...." not for ATS systems... (I could be wrong)