Main service enclosure used as a raceway?

Status
Not open for further replies.

tonype

Senior Member
Location
New Jersey
Service from meter passes through the enclosure to the generator transfer switch. Then back to the enclosure. Is this OK?
 

Attachments

  • DSCF7002 (1).JPG
    DSCF7002 (1).JPG
    1.6 MB · Views: 12

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It's certainly not nearest the entry of the service conductors into the structure so on that alone it's a violation.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Most often when the transfer switch is before the original service disconnect, the ATS becomes the service disconnect and has to be service rated.
Depending on the distance from the building entry point to the ATS it may violate the "nearest to point of entry" rule. But the details of that rule (allowed feet, etc.) are set by each AHJ. The term is not defined in the NEC.
You might end up having to route the generator and service wiring outside the building directly to the generator ATS.
 