Eclectic engineer
Member
- Location
- USA
- Occupation
- Engineer
During a site walk at a multi-family building, I noticed that the nameplate rating of the Main service entrance cabinet is 1600A at 120/208V.
However, when the deadfront was removed and I zoomed into the underground cable being fed to the main lugs, the conductor rating was
700 MCM AL ANACONDA 0 XLP 600 volts POWER CABLE.
I am assuming it is a 700 kcmil Aluminum conductor. When I looked up the NEC table, 700 kcmil is around 450A depending on temperature rating.
Am I interpreting this correctly?
Also, I am surprised that a 1600A main service cabinet is only being supplied by ~450A of power. Is this commonplace to find in electrical installations?
Thank you.