Attached sketch shows incoming service 200A, 4#3/0 into main fused service disconnect fused at 200A. Load side of the fused service disconnect 4#3/0 feeds the sub Panelboard 200A with main circuit breaker. The sub panelboard has main bonding jumper and service grounding electrode system.
I understand code requires main bonding jumper and grounding electrode system at 200A main fused service disconnect but its at sub panelboard. The fused disconnect does Not have equipment grounding conductor load side and the fused disco does not have main bonding jumper
Questions:
1. Fuses do not require equipment grounding conductor to operate correct so engineering wise what is attached should be ok correct?
2. Can the fused disco metallic enclosure be bonded thru neutral and not have objectionable current? Or it needs to have EGC? Speaking only Engineering wise
I understand code requires main bonding jumper and grounding electrode system at 200A main fused service disconnect but its at sub panelboard. The fused disconnect does Not have equipment grounding conductor load side and the fused disco does not have main bonding jumper
Questions:
1. Fuses do not require equipment grounding conductor to operate correct so engineering wise what is attached should be ok correct?
2. Can the fused disco metallic enclosure be bonded thru neutral and not have objectionable current? Or it needs to have EGC? Speaking only Engineering wise