I have 208/120V main service panelboard with main breaker 400A. The plans show the panelboard ground bus is bonded to the enclosure by manufacturer and the panelboard neutral bus is also bonded to enclosure by manufacturer without main bonding jumper.
I was wondering for those of you actually do the install or actually have seen field install inspection following questions:
1. I have seen panelboard where one bus is bonded to the enclosure by manufacturer and second one usually installed by contractors but not both buses bonded to enclosure by manufacturer. Do panels like one described above exists?
2. Suitable for use as service equipment only panelboard would it normally contain both neutral bar bonded to enclosure and ground bus bar bonded to enclosure? If not then how does it come typically?
3. Suitable for use as service equipment do both ground by and neutral bus come bonded to panelboard by manufacturer?
4. Would panel describe first paragraph suitable for use only as service equipment?
I was wondering for those of you actually do the install or actually have seen field install inspection following questions:
1. I have seen panelboard where one bus is bonded to the enclosure by manufacturer and second one usually installed by contractors but not both buses bonded to enclosure by manufacturer. Do panels like one described above exists?
2. Suitable for use as service equipment only panelboard would it normally contain both neutral bar bonded to enclosure and ground bus bar bonded to enclosure? If not then how does it come typically?
3. Suitable for use as service equipment do both ground by and neutral bus come bonded to panelboard by manufacturer?
4. Would panel describe first paragraph suitable for use only as service equipment?