jeff48356

Senior Member
Consider a 5000-square foot mansion being built, and it contains enough branch circuits to nearly fill two 200A service panels. What size main service would likely enter the meter outside? Would a 400-amp meter base be required, or could they use a 320-amp meter base that Home Depot carries? Which size service conductors would be likely be pulled into the meter base from the power company?
 

JFletcher

Senior Member
Location
Williamsburg, VA
I've helped build and wire 7,000+sq ft homes (mansions) that had full double kitchens, full double laundries, spa, pool, mancave, and electric aux heat in 3 ACs, with a generator panel. A 22kw genset can run most of it (90A). A 320A service will usually be fine unless everything is electric (water heater, heating, stove, etc.).

You need to do a load calculation to find out what you have.

As for the POCO, they run what they want to.
 