Main service switchboard

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have 1600A main service switchboard 277/480V plans say manufacturer provided main bonding jumper per NEC 2014 section 250.24(1)(4), 250.28(c), 250.8(a)(7).

I thought if manufacturer provides the main bonding jumper it is installed in factory. Has anyone ever had to install manufacturer provided main bonding jumper?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Ours always come factory installed but installing it in the field wouldn't be difficult.
MBJ.jpg
 