hhsting
- Glen bunie, md, us
- Junior plan reviewer
Attached sketch shows incoming 11 sets of 750kcmil service conductors into main service switchboards MLO with (3) 800 A main service breaker and (1) 2000A main service breaker
Each 800A breaker has grounding electrode conductor to external bus bar and 2000A breaker has grounding electrode conductor to external bus bar
The bus bar has bonding jumpers to grounding electrodes
The 800A main service disco has 400kcmil AL and 2000A main service disco has 500kcmil AL as main bonding jumper
Questions:
1. Switchboard is one assembly instead of providing one main bonding jumper each service disco has main bonding jumper. Anyome have any idea as to how each Main bonding jumper is sized because their is incoming electric utility service but then its all one assembly? How they go 400kcmil and 500kcmil?
2. Switchboard is one assembly so should not their be one main bonding jumper Not in individual ones? I see it as exception but its not required so how does one size each main bonding jumper in each main service disco?
Questions: