Main service switchboard

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached picture the red rectangle marked between utility meter and main breaker are they typically bus or cables?

f2c8b43d3dc15f638ab0151225782dd6.jpg
 
Can't really read the writing since the photo qualtiy is poor. If its all one peice of equipment that may be bolted together then busbars.
 
Where would the service entrance conductors be then in case like this?
The engineering firm our GC uses will include this on the one-line
1758720633350.png
Tucked down in the corner is the legend to specify wire types:
2500 - 6 sets 3 600kcmil and 1 350kcmil ground
2502 - 6 sets 4 600kcmil

The busbar sizes inside the switchgear weren't specified on the drawings I peeked at. I would imagine they're either on the submittal drawings, or perhaps incorporated as part of the UL listing.
 
Engineer is saying all wire into switchboard are electric utility. Then where would the service entrance conductors be? How would one size main bonding jumper?
 
Engineer is saying all wire into switchboard are electric utility. Then where would the service entrance conductors be? How would one size main bonding jumper?
Where is the service point?
At least for this site, service point is the step-down transformer (13.2k to 480Y277). You can't see it on the little snip I included, but there are no neutrals until we get almost to the point of use, at which point there's some kind of separately-derived source (Vertiv PDUs for IT gear, and a small-ish Square-D 480 to 208Y120 step-down right in front of the house panels).
 
Service conductors are whatever lands on the service disconnect. If they are bus bar and not wire type conductors then I believe cross sectional equivalent is used to determine minimum bonding jumper.
 
Engineer is saying all wire into switchboard are electric utility. Then where would the service entrance conductors be? How would one size main bonding jumper?
It would be rare that the utility would provide and install that wire. There would be no service entrance conductors in that case, and Note 2 to Table 250.66 would apply.
 