Attached picture the red rectangle marked between utility meter and main breaker are they typically bus or cables?
Can't really read the writing since the photo qualtiy is poor. If its all one peice of equipment that may be bolted together then busbars.
IMO 99.9% bus.Attach is little better pic.![]()
Agreed... all our drawings specifically call out number and size of wires when they exist.IMO 99.9% bus.
Agreed... all our drawings specifically call out number and size of wires when they exist.
Busbar trunking involved?Where would the service entrance conductors be then in case like this?
The engineering firm our GC uses will include this on the one-lineWhere would the service entrance conductors be then in case like this?

Where is the service point?Engineer is saying all wire into switchboard are electric utility. Then where would the service entrance conductors be? How would one size main bonding jumper?
Engineer is saying all wire into switchboard are electric utility. Then where would the service entrance conductors be? How would one size main bonding jumper?
At least for this site, service point is the step-down transformer (13.2k to 480Y277). You can't see it on the little snip I included, but there are no neutrals until we get almost to the point of use, at which point there's some kind of separately-derived source (Vertiv PDUs for IT gear, and a small-ish Square-D 480 to 208Y120 step-down right in front of the house panels).Where is the service point?
It would be rare that the utility would provide and install that wire. There would be no service entrance conductors in that case, and Note 2 to Table 250.66 would apply.Engineer is saying all wire into switchboard are electric utility. Then where would the service entrance conductors be? How would one size main bonding jumper?