Samardas
Member
- Location
- Los Angeles, CA, United States
- Occupation
- Electrical Engineer
An 800A 208/120V 3 Ph, 4 Wire service from the Utility is being asked for (Could also be 120/240V, 3 phase) in So California. Can the same switchboard have a 40 x 20A circuit breakers for distribution or do I need separate two (2) 400A Panels with 20A distribution breakers in each (up to 24 in each, total 48) that need to be fed from the Main 800A Switchboard. The situation is, there are 40 Truck Stalls in a parking lot each needing one 20A Receptacle and the Utility service switchboard is 800A. If all 40 x 20A breakers are allowed to be in the same Switchboard making it a distribution panel as well, then the customer does not need to buy separate panels. Your assistance will be highly appreciated. Thanks, Samar