brian john
Senior Member
- Location
- Leesburg, VA
I have a site with a main tie main, two lines up of gear, 13.2kv steps down to 480/277of gear connected with 3000 amp busway through a tie CB in each switchboard. In addition each switchboard is fed from a generator (two generators) through a generator circuit breaker.
All mains have GFP and there are neutral CT?s on each neutral feeder (residual GFP). The service neutrals are grounded at the main and the generator neutrals are grounded at the generator. There are four points where the neutral is grounded. This is a solid neutral throughout the distribution system.
While I realize there are different ways to control the GFP through the 4 mains (two utility, two generator), it seems that a single point of connection from the distribution system neutral to the main system electrode would be a better way to operate this system. At present there is neutral current on the EGC?s and while this current is low, the site loads are minimal at present.
Lastly to through a curve into the mix they have a 4-pole ATS for emergency lighting, so if the generator neutral bonds were lifted the neutral in the 4-pole ATS would need to be reconfigured.
I would think at a minimum the generators should not have the neutral bonded to ground?
What about the services neutral to ground bonds?
Lastly I see no where that any portion of this distribution system was ever tested to verify the GFP or distribution CB?s are functional. In particular the GFP?s as we have had multiple issues with main tie mains, where the switchboard inter-connects are not properly terminated.
All mains have GFP and there are neutral CT?s on each neutral feeder (residual GFP). The service neutrals are grounded at the main and the generator neutrals are grounded at the generator. There are four points where the neutral is grounded. This is a solid neutral throughout the distribution system.
While I realize there are different ways to control the GFP through the 4 mains (two utility, two generator), it seems that a single point of connection from the distribution system neutral to the main system electrode would be a better way to operate this system. At present there is neutral current on the EGC?s and while this current is low, the site loads are minimal at present.
Lastly to through a curve into the mix they have a 4-pole ATS for emergency lighting, so if the generator neutral bonds were lifted the neutral in the 4-pole ATS would need to be reconfigured.
I would think at a minimum the generators should not have the neutral bonded to ground?
What about the services neutral to ground bonds?
Lastly I see no where that any portion of this distribution system was ever tested to verify the GFP or distribution CB?s are functional. In particular the GFP?s as we have had multiple issues with main tie mains, where the switchboard inter-connects are not properly terminated.