What do you mean? The tie breaker was never closed?I have seen 100A main tie main configurations.
Kirk keys are simply a design decision. I have seen several M-T-M installed without any interlocking at all.
I have seen installations that were not interlocked in any manner at all allowing all main and tie breakers to be closed at the same time. Qualified employees and reliance on checklists were the only things preventing improper operation.What do you mean? The tie breaker was never closed?
what is the worst that could happen if all the breakers were closed at the same time? Its all synched in anyway.I have seen installations that were not interlocked in any manner at all allowing all main and tie breakers to be closed at the same time. Qualified employees and reliance on checklists were the only things preventing improper operation.
Unintentional paralleling is often not good. One issue is high fault current values. Another is unequal size sources and current division.what is the worst that could happen if all the breakers were closed at the same time? Its all synched in anyway.