Capacitorx
Member
- Location
- Dover,de
Hello,question at work I was adding some 20 amp circuits to 208 v 3 phase panel in an electric room at a hospital.it had a 30 amp main breaker at the bottom,so I was weary about adding more circuits because there were already like 8 to 10 20 a breakers in this square d panel with conductors landed on them so I was worried about exceeding breaker value and tripping it.so my question is it a nec violation to have breaker amounts and values that exceed the main breakers rating as long as the connected load does not exceed the main.the transformer feeding it was 9kva so the low voltage amp capacity was 25. I added 2 20 a boiler circiuts and a 20 amp circuit for 3 circ. Pumps..i think my forman was gambling that the other eight to 10 circuits were non-continuos loads but no one ever bothered to amp clamp anything ,so today I was told to add another 20 a circuit for a sequencer panel for the boilers I thought they must be retarded. I know my typing skills suck so please excuse me .