- Location
- St. Louis, MO
- Occupation
- Electrical Engineer
We're designing a new maintenance building where they are moving over existing machinery. Most of the machinery is listed at 120/240V 1ph, 240V 1ph, or 240V 3ph. We already designed for a 120/208V 3ph system. We thought it prudent to add an "Equipment Panel" at 240V/3ph delta, but can't agree on how to ground it. Corner ground? Add "ground fault detectors" in the main circuit breaker? If we design a 240V/3ph panel, establish an earth ground for the ground bus, then there is no ground reference in the 3 hot conductors, right? The equipment ground conductor grounding the metal casing of the equipment does nothing to protect the person leaning on it, right?
Another option is to provide a 120/240V 3ph hi-leg delta panel without a neutral bus. Less expensive transformer. And you'll have 120V to ground on 2 of the 3 phases. I believe 3rd phase will be 208V to ground, but still better than corner ground with 240V to ground.
Any input would be most appreciated.
Another option is to provide a 120/240V 3ph hi-leg delta panel without a neutral bus. Less expensive transformer. And you'll have 120V to ground on 2 of the 3 phases. I believe 3rd phase will be 208V to ground, but still better than corner ground with 240V to ground.
Any input would be most appreciated.