For a major repair garage without any pits or below floor areas, the ventilation required to make the area non-classified is a lot (1 cubic foot per minute per square foot of floor area). That's usually about 4 air changes per hour. That's a lot of air to heat or cool, especially in the Midwest.
But if the ventilation isn't provided, everything becomes Class 1, Division 2. The entire service area and even the offices and restrooms since there are doors into the service area. This seems impossible to deal with. I assume then that any welding or grinding, battery charging, or anything that might cause a spark would be prohibited. Even an office copy machine wouldn't be allowed to sit on the floor (its not going to be listed for a class 2 location.) How can I even provide receptacles, since a cord is almost certain to hang from the outlet down to something within the classified area.
Are there any other options besides providing the ventilation or classifying the entire building?
Is it possible to designate one area for major repair and just ventilate that area with the 1 CU/M per SF? Or maybe its possible to designate one area for anything that could produce sparks, and ventilate that area?
But if the ventilation isn't provided, everything becomes Class 1, Division 2. The entire service area and even the offices and restrooms since there are doors into the service area. This seems impossible to deal with. I assume then that any welding or grinding, battery charging, or anything that might cause a spark would be prohibited. Even an office copy machine wouldn't be allowed to sit on the floor (its not going to be listed for a class 2 location.) How can I even provide receptacles, since a cord is almost certain to hang from the outlet down to something within the classified area.
Are there any other options besides providing the ventilation or classifying the entire building?
Is it possible to designate one area for major repair and just ventilate that area with the 1 CU/M per SF? Or maybe its possible to designate one area for anything that could produce sparks, and ventilate that area?