Make it make sense - OCPD Requirements for small transformers

Tip DS

I'm here.
Location
The Great Meme State
Occupation
Electrical Engineer
1710860019258.png

Notice that when you choose to use primary AND secondary protection for a transformer, your primary protection maximum rating goes UP in all instances, except for small transformers. For those, you can use a big OCPD for primary-only protection, but if you're going to double up on protection, you have to use a SMALLER OCPD on the primary.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Two comments:

- Just because you choose to provide secondary protection doesn't mean you have to use the second line on the table. You can still use primary protection of up to 300% on a transformer with a current of 2A or less.
- For such a transformer, the second line still allows greater flexibility (primary protection at 600% or 400%) for some types of transformers because of Note 3.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This is one of the most poorly written code articles no wonder it causes a great deal of confusion.
 