megloff11x
Senior Member
We're looking to sell in Europe and need to set up testing for 400V 3-phase at 50Hz for up to 250A. Back when my work was lab instruments at another job, we paid a new car price for a device that generated 80-264V, 40-80Hz, and I think up to 20A, for testing out small instruments (wall outlet power). It was the size of a computer tower.
We had enough problems with the 50Hz issue - brownout detect circuits tripping because 50Hz allowed more sag, loss of compliance Voltage over the extra 16% time between peaks - the canned calculations for capacitor size didn't allow enough margin. Problems in Japan (100V nominal and serious power quality issues), small transformers rated for 50Hz that really wouldn't work at that frequency and would just draw >10x their 60Hz rated current until the fuse blew or they melted, etc. We thought it prudent to test under as close to actual conditions as we could make. We had these and enough other unexpected problems that we bought the device and learned not to flaunt Murphy's laws. And we learned a lot of interesting little things we never expected would happen.
For huge scale industrial machinery, what's the way? The easiest may be a 208 or 480V to 400V transformer, but you are still at 60Hz. If you think frequency won't cause problems, that may be the least expensive.
The only other way I can think of that would be cost effective at these high current loads is to use a generator and run it slower to make 50Hz power. I would think that a PWM system might have too many noise issues and cost too much, but the prices & power quality may have improved.
Has anyone set something up like this at an industrial machine manufacturer, and can you elaborate?
We had enough problems with the 50Hz issue - brownout detect circuits tripping because 50Hz allowed more sag, loss of compliance Voltage over the extra 16% time between peaks - the canned calculations for capacitor size didn't allow enough margin. Problems in Japan (100V nominal and serious power quality issues), small transformers rated for 50Hz that really wouldn't work at that frequency and would just draw >10x their 60Hz rated current until the fuse blew or they melted, etc. We thought it prudent to test under as close to actual conditions as we could make. We had these and enough other unexpected problems that we bought the device and learned not to flaunt Murphy's laws. And we learned a lot of interesting little things we never expected would happen.
For huge scale industrial machinery, what's the way? The easiest may be a 208 or 480V to 400V transformer, but you are still at 60Hz. If you think frequency won't cause problems, that may be the least expensive.
The only other way I can think of that would be cost effective at these high current loads is to use a generator and run it slower to make 50Hz power. I would think that a PWM system might have too many noise issues and cost too much, but the prices & power quality may have improved.