Hello,
We do electrical maintainence at a large mall. We have incounter an intresting problem. We have been called out several times for a main breaker in the mdp tripping, seimens 150amp 3phase 480v. It feeds a store that has an I line breaker panel with 1 150amps 3 phase 480volt main breaker and 2 smaller ac loads. The distance is approx. 30ft some which is underground. This panel also carries a breaker for a step down transformer to 120/208, and carries various lighting loads in the store.
The 480 volt panel does not have a neutral feeding the store since there isn't any 277 load.
We believe that the mdp for the mall is grounded and bonded together at that point.
Do we still need a neutral at the store's panel? If yes, would this contribute to the main in the store not tripping?
Another option would be the aic is faster at the mdp main instead of the stores main.
any ideas?
Ampman
ampman
We do electrical maintainence at a large mall. We have incounter an intresting problem. We have been called out several times for a main breaker in the mdp tripping, seimens 150amp 3phase 480v. It feeds a store that has an I line breaker panel with 1 150amps 3 phase 480volt main breaker and 2 smaller ac loads. The distance is approx. 30ft some which is underground. This panel also carries a breaker for a step down transformer to 120/208, and carries various lighting loads in the store.
The 480 volt panel does not have a neutral feeding the store since there isn't any 277 load.
We believe that the mdp for the mall is grounded and bonded together at that point.
Do we still need a neutral at the store's panel? If yes, would this contribute to the main in the store not tripping?
Another option would be the aic is faster at the mdp main instead of the stores main.
any ideas?
Ampman
ampman