I am trying to make sense of when I need one vs the other.

I have a indoor hvac unit with a fan that I am hooking up. It is 208v/1 7.7 amps.

How do I know which one I need?

Thanks

Hoyt:-?
 
1st, I would make sure you actually need a "starter" at all. Many 1 phase units already have some type of overload protection.

I typed this far then saw Bob's answer... and his question is the next pertinent one so I will bow out.....
 
Well... its a Blower Coil unit, and I guess i need to ask the HVAC engineer how is it controlled.

Would it be possible to provide a Man with auxilary contacts for control?
 
Hoyt said:
Would it be possible to provide a Man with auxilary contacts for control?

Yes. Small toggle switch units don't offer aux contacts, but bigger manual ones do.
 
A Manual starter means that the control of it, i.e. how the motor is turned on and off, is done MANUALLY, meaning a human must put their fingers on the switch to operate it. Aux. contacts can SIGNAL the status of that switch, but cannot CONTROL it.

A magnetic starter provides a coil that can be energized and de-energized by some other electrical means be it a control system, such as your HVAC control system, or even a separate / remote manually operated switch such as push buttons or a selector switch.

In addition, you must also consider the desired operation after a power failure. On restoration of power, do you want that motor to automatically come back on? if so, is there a danger of someone being in contact with moving parts if it does? If automatic restart is not desireable, you need to use a mag. starter or an Under Voltage Trip on a manual starter. The UV Trip option however will also require a person to manually reset it after the power failure.
 
Hoyt said:
Well... its a Blower Coil unit, and I guess i need to ask the HVAC engineer how is it controlled.

It would be very unusual for a fan coil unit to use a manual motor starter. The large majority (if not all) use magnetic starters so that they can be controlled remotely with low voltage.
 