I am working on a project in which i have to run 4 MV feeders
4X( 3X1C-240 sq mm) unarmoured Aluminum cable in 6 Inch Dia conduit.
The overall dia of one aluminum cable as i get from cable table is 35 mm dia.
The conduits will b burried 2ft Below grade.

How would i calculate the manhole size..

If some one can show the calculation work, it will really be helpful.

Regards.

Sent from my GT-I9300I using Tapatalk
 

Sajid khan

Senior Member
Location
Pakistan
I am working on a project in which i have to run 4 MV feeders
4X( 3X1C-240 sq mm) unarmoured Aluminum cable in 6 Inch Dia conduit.
The overall dia of one aluminum cable as i get from cable table is 35 mm dia.
The conduits will b burried 2ft Below grade.

How would i calculate the manhole size..

If some one can show the calculation work, it will really be helpful.

Regards.

Sent from my GT-I9300I using Tapatalk
4 MV feeder ( 12 Nos 240 Sq
mm Al conductor) in 4 Nos 6 inch Dia conduit.

Sent from my GT-I9300I using Tapatalk
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
If you need the duct bank size it is one question. However, the manhole dimensions depend less on the duct bank size but more on the ergometric arrangement.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
One duct of 6" can accommodate 2 feeders so you'll need 2 ducts.
The minimum ductbank dimensions will be 550 *300 mm. and
the dimensions of the manhole will be 1.5m at the input of the cables and 1m in front of the entrance.The height 6 ft.1.83 m according to NESC 2007 RULE 323. Manholes, handholes, and vaults
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
If you intend to run each feeder in a separate conduit [duct] the ductbank cross section will be 550*550 mm. However, the height of the manhole has to be the same 1.83 as per NESC. Manhole minimum inside dimensions.jpg
These are the minimum inside dimensions.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
It is very interesting Bill4477. However, it is about pipe line visiting manhole and not for electrical cable ducts.
 

Dale001289

Senior Member
Location
Georgia
I am working on a project in which i have to run 4 MV feeders
4X( 3X1C-240 sq mm) unarmoured Aluminum cable in 6 Inch Dia conduit.
The overall dia of one aluminum cable as i get from cable table is 35 mm dia.
The conduits will b burried 2ft Below grade.

How would i calculate the manhole size..

If some one can show the calculation work, it will really be helpful.

Regards.

Sent from my GT-I9300I using Tapatalk

Since you're using 240 sq mm I assume this is an IEC project vs NEC? For domestic US projects NEC Art 110.70 in addition to the NESC would be a helpful resource.
With only 4, 150mm diameter conduits, your manhole wont have to be excessively large. But there are a few basic parameters you need to consider. Will there be a fixed ladder? Will there be a sump pump? Will there be future cables/conduit? Are you in a Classified area, i.e. Zone 2 (Div 2)? And last but most important - have you determined cable bend radius requirements?
 

RumRunner

Senior Member
Location
SCV Ca, USA
Occupation
Retired EE
I cannot open this.. is it abailable in PDF??

Sent from my GT-I9300I using Tapatalk

The above url is a proprietary document file for manhole designers.

You can use the address: www.scribd.com to gain access to the document.

If the link is not hyper, just type it on the prompt. Keep in mind that most documents are for design engineers and may require registration.

All the best.
 

Sajid khan

Senior Member
Location
Pakistan
Thanks for the information
I am also a Design Electrical engr.
The above url is a proprietary document file for manhole designers.

You can use the address: www.scribd.com to gain access to the document.

If the link is not hyper, just type it on the prompt. Keep in mind that most documents are for design engineers and may require registration.

All the best.

Sent from my GT-I9300I using Tapatalk
 

Sajid khan

Senior Member
Location
Pakistan
Yes this is an IES project.
I would refer to NEC also for reference as u mentioned.

I have much concerned about the depth of the manhole. Considering the bending radius of the cable, it would not be much, Generally 12 times Overall Dia of the cable which in this case would be 35x12=420 mm So if we consider the depth of the manhole to be 900 mm i think would be pretty enough.
Since you're using 240 sq mm I assume this is an IEC project vs NEC? For domestic US projects NEC Art 110.70 in addition to the NESC would be a helpful resource.
With only 4, 150mm diameter conduits, your manhole wont have to be excessively large. But there are a few basic parameters you need to consider. Will there be a fixed ladder? Will there be a sump pump? Will there be future cables/conduit? Are you in a Classified area, i.e. Zone 2 (Div 2)? And last but most important - have you determined cable bend radius requirements?

Sent from my GT-I9300I using Tapatalk
 

Dale001289

Senior Member
Location
Georgia
Yes this is an IES project.
I would refer to NEC also for reference as u mentioned.

I have much concerned about the depth of the manhole. Considering the bending radius of the cable, it would not be much, Generally 12 times Overall Dia of the cable which in this case would be 35x12=420 mm So if we consider the depth of the manhole to be 900 mm i think would be pretty enough.

Sent from my GT-I9300I using Tapatalk

Yes, 12 times OD is about right - and is consistent with NEC Article 300.34, by the way. The manhole is really more of a 'hand hole' since your proposing only a 3'-0" depth. This would put your conduit duct at about 24" depth when it enters the hand hole - depth is also consistent with NEC Table 300.50, btw. It should be wide enough to pull cable out - then make a loop in order to reenter the hole without damage to cable.
 

Sajid khan

Senior Member
Location
Pakistan
Yes, 12 times OD is about right - and is consistent with NEC Article 300.34, by the way. The manhole is really more of a 'hand hole' since your proposing only a 3'-0" depth. This would put your conduit duct at about 24" depth when it enters the hand hole - depth is also consistent with NEC Table 300.50, btw. It should be wide enough to pull cable out - then make a loop in order to reenter the hole without damage to cable.
Thanks will check the mentioned NEC Articles

Sent from my GT-I9300I using Tapatalk
 