I am installing a 400 amp residential service. I do not seem to be able to find a 400 amp manual transfer switch with an integral OCPD. I am limited severely with space and would like to keep pieces of equipment at a minimum. I am installing first the Meter can, next the Manual transfer switch and then next to it the 400 amp load center, all 3 pieces of equipment are side by side. Since I cannot find the manual transfer switch as described I am thinking that installing one without integral OCPD, and then the loadcenter with a 400 amp main breaker, may be all I need for this install. The manual transfer switch is rated for use a service equipment and has an "off" position. Question:#1- are the conductors from the service lateral to and through the manual transfer switch to the Main breaker on the loadcenter considered the service entrance conductors? #2 Would the transfer switch be considered the service disconnect and the Main breaker in the loadcenter the OCPD satisfying article 230.91?