I'm working on a project where the client would like to explore adding a connection point for a roll up charger. The current setup new 1600A, 480V service entrance switchboard with (4) sets 600KCMIL per phase. We are considering a service entrance rated generator docking station with a MTS ahead of the 1600A switchboard. I'm trying to think about what size to make this.
For these gen docking stations with MTS, it looks like there is a cut off point at 1200A and once you go bigger than that (up to 1600A) you have to look at getting multiple sections or other inconvenient setups.
They're not sure on what generator size they'd be able to provide, but if they're looking at something like the CAT XQ600 600kW/750kVA I would think that I only need to size the docking station at 1200A {750kVA/(480V*1.732)=902A; 902A*1.25=1127A} as long as it can support my (4) 600KCMIL per phase, right? Is there something else I should consider for this? Do I NEED a 1600A MTS to match my switchboard?
For these gen docking stations with MTS, it looks like there is a cut off point at 1200A and once you go bigger than that (up to 1600A) you have to look at getting multiple sections or other inconvenient setups.
They're not sure on what generator size they'd be able to provide, but if they're looking at something like the CAT XQ600 600kW/750kVA I would think that I only need to size the docking station at 1200A {750kVA/(480V*1.732)=902A; 902A*1.25=1127A} as long as it can support my (4) 600KCMIL per phase, right? Is there something else I should consider for this? Do I NEED a 1600A MTS to match my switchboard?