Manual Transfer Switch

Status
Not open for further replies.

Fitzdrew516

Senior Member
Location
Cincinnati, OH
Recently I had designed a 3000A service to a facility. I included GFP on the main gear per code, but recently there have been some changes in the field that I want to clarify. The contractor and the client have put forth a plan to install a manual transfer switch outside the building right before the conductors enter the main gear. Questions below -

1) Does the transfer switch need to have GFP? I assume it will have to incorporate this now if there is a disconnect on the transfer switch considering that would technically be the service disconnect now.

2) The contractor had selected a 3 pole transfer switch. I know there is some give and take as to which is better: 3 or 4 pole. Does anyone have any input as to why we should go with one that disconnects the neutral as well?

Thanks,
- Drew
 

Fitzdrew516

Senior Member
Location
Cincinnati, OH
If the MTS is upstream of what you had acting as the main, will the MTS be the new service rated disconnect?

I'm not sure whether or not the MTS will have a disconnect on it, but every one I've ever seen has had a disconnect on it so I assumed that this one would and would now be acting as the main for the service due to it being upstream.
 

Fitzdrew516

Senior Member
Location
Cincinnati, OH
I just received this breakdown. Looks like they are including GFP so that alleviates my first concern. Looks like they are opting for a 3 pole transfer switch though. Any qualms with this?
 

Attachments

  • Manual Transfer.JPG
    Manual Transfer.JPG
    140.6 KB · Views: 1

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
At 3000A, that "manual transfer switch" is two interlocked circuit breakers, in this case, C-H Insulated Case Power Breakers. It's only called "manual" because they leave out the components that monitor the line and generator to transfer automatically, you have to send it commands via another control system, or walk up to it and push the buttons.
 

Fitzdrew516

Senior Member
Location
Cincinnati, OH
At 3000A, that "manual transfer switch" is two interlocked circuit breakers, in this case, C-H Insulated Case Power Breakers. It's only called "manual" because they leave out the components that monitor the line and generator to transfer automatically, you have to send it commands via another control system, or walk up to it and push the buttons.

Correct, but with it being upstream of the old service disconnect, then this would now be the new service disconnect, correct?
 

dkidd

Senior Member
Location
here
Occupation
PE
Correct, but with it being upstream of the old service disconnect, then this would now be the new service disconnect, correct?

Yes. Things to consider include removing the existing neutral to ground bond, and

230.91 Location. The service overcurrent device shall be
an integral part of the service disconnecting means or shall
be located immediately adjacent thereto.
 

bsmith8691

Member
Location
Ellington, CT
It does have to be listed and rated as service entrance equipment. Unless I've missed something, on a stationary standby you don't need the fourth pole to be disconnected.

Sent from my XT1254 using Tapatalk
 
Status
Not open for further replies.
Top