I think this will be a stupid question, and I'm rusty on this subject, please bear with me, but if the shop subpanel will require an isolated neutral, how can you do that from the disconnect mounted on the pole, since it is fed directly from the meter?
Service is created at the pole. Meter and disconnect and breaker, neutral and ground tied together at panel on pole. I don't see a issue unless you are talking about room for conductors. I am sure the OP will address that.