K kevco New member Oct 7, 2006 #1 Im going to be doing a service for a friend on is manufactured home and im curious if the disconnect on the pole has to be fused or not thanks kevin
Im going to be doing a service for a friend on is manufactured home and im curious if the disconnect on the pole has to be fused or not thanks kevin
R RUWired Senior Member Location Pa. Oct 7, 2006 #2 Kevco, 230.91 Location The service overcurrent device shall be an integral part of the service disconnecting means or shall be located immediately adjacent thereto. Rick
Kevco, 230.91 Location The service overcurrent device shall be an integral part of the service disconnecting means or shall be located immediately adjacent thereto. Rick
B benaround Senior Member Location Arizona Oct 7, 2006 #3 Kevco, Start at 550.32(B) then adapt to your condition.