Does the electric service coming from a power pole with a meter and disconnect have to be within 30 feet of the manufactured home as in NEC 550
550.32 Service Equipment.
(A) Mobile Home Service Equipment. The mobile home service equipment shall be located adjacent to the mobile home and not mounted in or on the mobile home. The service equipment shall be located in sight from and not more than 9.0 m (30 ft) from the exterior wall of the mobile home it serves. The service equipment shall be permitted to be located elsewhere on the premises, provided that a disconnecting means suitable for service equipment is located in sight from and not more than 9.0 m (30 ft) from the exterior wall of the mobile home it serves. Grounding at the disconnecting means shall be in accordance with 250.32.
But from this disconnect you must run 4-wires, and the grounding conductor has to be insulated.Exception: Where a feeder is installed between service equipment and a disconnecting means as covered in 550.32(A), it shall be permitted to omit the equipment grounding conductor where the grounded circuit conductor is grounded at the disconnecting means as required in 250.32(B).
If you have a disconnect on a pole then go to the disconnect for the home it must be 4 wire. 2008 NEC.
In Ohio we kept the 2005 NEC for manf. homes so you only need a 3 wire in the above example.
Mike, it is still allowed in the 2008, take a look at 550.33(A)(2) exception, they just added another number to the section (2)
Still there.
And if the MH is not on a permanent foundation it would fall under Federal HUD codes anyway which still allow it also, CFR 24 Part 3280.800
Not understanding what you are saying.
As I read it a 3 wire is allowed if it is existing. If not 4 wire is required.
My point is that the 2005 allows a three wire between structures and the 2008 requires a 4 wire.
again see above, the wording of 550.33 has not changed between 2008 and 2005.So if you had a disconnect on a pole and the disconnect required at the home, under the 2008 you have to use 4 wire. If you are using the 2005 you could use three wire between the disconnects. Assuming no parallel paths.
550.33(A)(2)Exception: Where a feeder is installed between service equipment and a disconnecting means as covered in 550.32(A), it shall be permitted to omit the equipment grounding conductor where the grounded circuit conductor is grounded at the disconnecting means as required in 250.32(B).
Agreed no changes in 550.33.
I am talking about 250.32(B).
Existing is in the exception under 550.33(A)(2).
550.33(A)(2)Exception: Where (For) a (an existing)[this is missing from your quote] feeder is installed between service equipment and a disconnecting means as covered in 550.32(A), it shall be permitted to omit the equipment grounding conductor where the grounded circuit conductor is grounded at the disconnecting means as required in 250.32(B).
I am using the 2008 handbook. Do not have the 2008 NEC in front of me. Is it missing "an existing"?
? 3280.801 Scope.
(a) Subpart I of this part and Part II of Article 550 of the National Electrical Code (NFPA No. 70?2005) cover the electrical conductors and equipment installed within or on manufactured homes and the conductors that connect manufactured homes to a supply of electricity.
(b) In addition to the requirements of this part and Part II of Article 550 of the National Electrical Code (NFPA No. 70?2005), the applicable portions of other Articles of the National Electrical Code must be followed for electrical installations in manufactured homes. The use of arc-fault breakers under Articles 210.12(A) and (B), 440.65, and 550.25(A) and (B) of the National Electrical Code, NFPA No. 70?2005 is not required. However, if arc-fault breakers are provided, such use must be in accordance with the National Electrical Code, NFPA No. 70?2005. Wherever the requirements of this standard differ from the National Electrical Code, these standards apply.