Manufactured HUD Home Disconnect Question

Status
Not open for further replies.

wilsonballew

New User
Location
Colorado
Occupation
Homeowner
Hello All - I am installing a new manufactured HUD home on my property. The main service meter is a pedestal setup that is about 130 feet from where the home will be placed. We ran underground direct bury wire from the meter pedestal to an emergency disconnect [not attached to the home but about 20 feet from the home on a pole mount] and then continued underground from the emergency disconnect to a point where the cable will enter under the home and feed into the main panel. We had a partial rough inspection today and the inspector noted:

1) Feeder disconnect means at new modular will need to be followed per NEC 2023 article 225.31(A)(B)
2) Feeders will need to remain 18" underground in a conduit before turning up into new modular nearest point of entrance of the conductors or install a disconnect on the exterior of the dwelling.
Feeder conductors will be considered outside of the building unless one of the following conditions are met per NEC 2023 article 230.6 (1-5).


Do I understand correctly for number (1) the feeder disconnect can be the main breaker in the main panel inside the home?

Regarding number (2), I am unclear about installing an exterior disconnect on the building and how that mitigates the need to run the cable under the home buried 18" deep in conduit. I was always planning on running the conduit from the entry point under the home to the main panel conduit connection but I was not planning on burying the conduit; if I understand the instructions, I must bury the conduit if I don't have an exterior disconnect and if I do have an exterior disconnect, I don't need to bury the conduit?

Inspector also noted will need a surge protection device - I guess this is something I missed in the 2023 NEC [used in Colorado]. This is a brand new manufactured home and I don't know if it will come from the factory with surge protection built-in to the main panel [home not delivered yet].

Thanks for any clarification.
 
Forum rules prevent us from assisting you, as we don’t know what else you are not asking. An electrical contractor would be my suggestion to assist you
 