Hi All,
I originally posted one similar to this in the NEC section but I think it would be better here.
This concerns a Type 334 cabinet used for data aquisition and ramp metering along the highway--so any traffic guys jump in--
I need to find out where it says that in a cabinet(Not UL listed) the manufacturer is exempt from the NEC wire size.
Situation is as follows;
From a 30 amp buss there is a 16 AWG wire that goes to a term strip--from there it goes to to an 18AWG wire to one side of a set of contacts on an ice cube relay. Then across the relay suppling power to a flasher unit which flashes the warning signs.
We have thousands of these and they are built to Cal-Trans spec so there are thousands more out there. He wants to hit it along with some other problems and have the manufacturer "bring it up to code".
Somewhere in the back of my head is a tickle that says this is ok but can't find him a referance. if you need any more info please let me know!
I originally posted one similar to this in the NEC section but I think it would be better here.
This concerns a Type 334 cabinet used for data aquisition and ramp metering along the highway--so any traffic guys jump in--
I need to find out where it says that in a cabinet(Not UL listed) the manufacturer is exempt from the NEC wire size.
Situation is as follows;
From a 30 amp buss there is a 16 AWG wire that goes to a term strip--from there it goes to to an 18AWG wire to one side of a set of contacts on an ice cube relay. Then across the relay suppling power to a flasher unit which flashes the warning signs.
We have thousands of these and they are built to Cal-Trans spec so there are thousands more out there. He wants to hit it along with some other problems and have the manufacturer "bring it up to code".
Somewhere in the back of my head is a tickle that says this is ok but can't find him a referance. if you need any more info please let me know!