• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Manufacturers install instructions

nizak

Senior Member
Have a EV charger that says that the E.G.C. needs to be the same wire gauge as the ungrounded conductors.

Circuit is protected at 100 amps w/ #3 thhn conductors.

Does there install instructions supersede the NEC when it comes to grounding?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Does there install instructions supersede the NEC when it comes to grounding?
Generally speaking, the more stringent of either applies, so yes, they can.

Kinda like requiring copper where aluminum is otherwise compliant.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Sounds like the requirements that hot tub mfg spec for the EGC. I have never installed an EGC same size as the line conductors and never been called on it.
 

ppsh

Member
Location
CA
Occupation
Electrician
Junction box or panel before the charger, convert from Al to CU, and upsize the EGC?
 

retirede

Senior Member
Location
Illinois
I’m

Grizzl-E
GRU-077-W-HW-25DJ80-A-GB

OK. I looked at the installation manual. It looks to me like they copied the section on grounding from their smaller, cord and plug models. They likely didn’t intend to require a full size EGC on this unit. Unfortunately, that doesn’t mean you can ignore it.

4504e8f0db8ab51608a1fe202665e761.jpg
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Agreed. I don't remember an inspector ever asking to see the installation instructions for anything.
Larry I remember one of your first replies to me on my question on wiring a tanning bed was R.T.F.M.
😆 and my reply was if I had T.F.M I would have read T.F.M.
Set off quite a few replies from "what does that mean?"
To other variations of it. 😆
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Larry I remember one of your first replies to me on my question on wiring a tanning bed was R.T.F.M.
😆 and my reply was if I had T.F.M I would have read T.F.M.
Set off quite a few replies from "what does that mean?"
To other variations of it. 😆
But you weren't the inspector, right?
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
It looks to me like they copied the section on grounding from their smaller, cord and plug models. They likely didn’t intend to require a full size EGC on this unit. Unfortunately, that doesn’t mean you can ignore it.
I don't know, makes me think that all of Section 4.2 is in error. I'm in favor of the idea that you can ignore obviously erroneous parts of the manual.

This also raises the question of whether the entire installation manual counts as part of the "listing and labeling" for the purposes of 110.3(B).

Cheers, Wayne
 

garbo

Senior Member
To my reasoning installing a ground wire the same size as line wires ( larger then 10 guage ) is a waste of money. On a short the ground wire only carries current for milliseconds. Like other poster said never been called on reduced ground found in every larger NM cable. Instructions demanding such things are too often written by electronic nerds Who do not know the code.
 
Top