I’mWhat brand and model number?
Grizzl-EWhat brand and model number?
Generally speaking, the more stringent of either applies, so yes, they can.Does there install instructions supersede the NEC when it comes to grounding?
Agreed. I don't remember an inspector ever asking to see the installation instructions for anything.I have never installed an EGC same size as the line conductors and never been called on it.
I’m
Grizzl-E
GRU-077-W-HW-25DJ80-A-GB
Junction box or panel before the charger, convert from Al to CU, and upsize the EGC?
Larry I remember one of your first replies to me on my question on wiring a tanning bed was R.T.F.M.Agreed. I don't remember an inspector ever asking to see the installation instructions for anything.
But you weren't the inspector, right?Larry I remember one of your first replies to me on my question on wiring a tanning bed was R.T.F.M.
and my reply was if I had T.F.M I would have read T.F.M.
Set off quite a few replies from "what does that mean?"
To other variations of it.![]()
No. I was in quality control at the time so reading manuals on equipment was one of my tasks.But you weren't the inspector, right?
I don't know, makes me think that all of Section 4.2 is in error. I'm in favor of the idea that you can ignore obviously erroneous parts of the manual.It looks to me like they copied the section on grounding from their smaller, cord and plug models. They likely didn’t intend to require a full size EGC on this unit. Unfortunately, that doesn’t mean you can ignore it.