If you receive a non-standard amperage size from the manufacturer for their equipment's MOCP, such as 106A, is it acceptable to use the next size up breaker (per 240.4) in this case 110A or do I need to use 100A?
Thanks,
Keri
240.4 does not apply to this.
Maximum is maximum. You cannot use more than the max.
If you receive a non-standard amperage size from the manufacturer for their equipment's MOCP, such as 106A, is it acceptable to use the next size up breaker (per 240.4) in this case 110A or do I need to use 100A?
Thanks,
Keri
I never seen a Max OCPD value listed on a label that did not correspond to a standard value. I'm not even sure if the listing standard would allow this. Do you have such a case?
I have seen equipment like generators with non-standard breaker sizes. I expect that if you want to pay for it, you can get any current rating that you want to.
The 489 standard only permits specific amp ratings?It may be difficult to convince the manufacturer today to do a special calibration because of the automated manufacturing process used today.But over 30 yesrs ago in the good old days such modifications were commonly avsilable. But the UL489 listing is lost.
The 489 standard only permits specific amp ratings?