I have been reading the forum and the net to answer a question on making calculations for a marina. The typical design of a Marina these days is Shore power (480 VAC 3 Phase) Coming out to a Substation (225 KVA) for this example and then the substation having a 220/120 Circuit Panel Supplying Pedestals. A Pedestal typically has a 50A and a 30A Receptacle on Each side. A circuit breaker may power more than one pedestal so this side of the substation may have several circuit breakers. Now here is the calculation question based on Article 555.12 of the NEC. It says that the demand factors as set forth in Table 555.12 shall be permitted for each service and or feeder circuit supplying shore power for Boats with the modifications of notes 1 and 2. For this example, lets say there are 30 Receptacles that are powered from this substation and each circuit breaker on the substation feeds 8 receptacles. Based on this and the word feeder circuit in the code, I would assume that the 70% factor would be used on the diversity of the Substation. Because it uses the words feeder circuit, that seems misleading on the lower voltage side because each of these are branch circuits. So do you use the same table for Demand Factors for these individual branch circuits? If so each branch circuit in the example would use 90%. Any Thoughts??