Marina dock stanchions with GFCI outlets.

Merry Christmas

DENTRAy

New User
Location
07716
Occupation
Electrician
If a GFCI receptacle on a dock stanchion fails, does the Marina have to replace the device? My Marina is refusing to replace the GFCI receptacles on the stanchions, because they said the GFCI gets corroded, and they don't want to replace them anymore.

Thank you,
Dennis Traynor.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

I would imagine they are responsible if your lease agreement includes power availability.

If so, they're in breach of contract.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The code does not require power on the dock, and only tells you how to install power on the dock if someone wants power, so it comes down to the issue Larry raised in the previous post.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Is the failed GFCI a weather resistant type (WR)? WR GFCIs hold up better as are more corrosion resistant.
 